Property Inspection Report

Client(s):  Mr Smith
Property address:  Big Bear Lake, Ca
Inspection date:  Tuesday, August 29, 2017

This report published on Thursday, October 26, 2017 11:47:21 PM CDT

This report is the exclusive property of this inspection company and the client(s) listed in the report title. Use of this report by any unauthorized persons is prohibited.
How to Read this Report
This report is organized by the property's functional areas.  Within each functional area, descriptive information is listed first and is shown in bold type.  Items of concern follow descriptive information. Concerns are shown and sorted according to these types:
Concern typeSafetyPoses a safety hazard
Concern typeMajor DefectCorrection likely involves a significant expense
Concern typeRepair/ReplaceRecommend repairing or replacing
Concern typeRepair/MaintainRecommend repair and/or maintenance
Concern typeMinor DefectCorrection likely involves only a minor expense
Concern typeMaintainRecommend ongoing maintenance
Concern typeEvaluateRecommend evaluation by a specialist
Concern typeCommentFor your information

Click here for a glossary of building construction terms.Contact your inspector If there are terms that you do not understand, or visit the glossary of construction terms at http://www.reporthost.com/glossary.asp

Table of Contents
General Information
Grounds
Exterior and Foundation
Roof
Electric
Plumbing / Fuel Systems
Water Heater
Heating, Ventilation and Air Condition (HVAC)
Fireplaces, Stoves, Chimneys and Flues
Kitchen
Bathrooms, Laundry and Sinks
Interior, Doors and Windows

View summary


General Information
Return to table of contents

Report number: 1728
Present during inspection: Client
Client present for discussion at end of inspection: Yes
Weather conditions during inspection: Sunny
Temperature during inspection: Cool
Payment method: Credit card
Type of building: Mobile home
Buildings inspected: One house
Number of residential units inspected: 1
Age of main building: 38
Source for main building age: Realtor
Front of building faces: East
Main entrance faces: East
Occupied: Yes

1) Structures built prior to the mid 1980s may contain lead and/or asbestos. Lead is commonly found in paint and in some plumbing components. The EPA does not recognize newer coats of paint as encapsulating older coats of lead-based paint. Asbestos is commonly found in various building materials such as insulation, siding, and/or floor and ceiling tiles. Laws were passed in 1978 to prohibit usage of lead and asbestos, but stocks of materials containing these substances remained in use for a number of years thereafter. Both lead and asbestos are known health hazards. Evaluating for the presence of lead and/or asbestos is beyond the scope of this inspection. Any mention of these materials in this report is made as a courtesy only, and meant to refer the client to a specialist. Consult with specialists as necessary, such as industrial hygienists, professional labs and/or abatement specialists for this type of evaluation. For information on lead, asbestos and other hazardous materials in homes, visit:
http://www.reporthost.com/?EPA
http://www.reporthost.com/?CPSC
http://www.reporthost.com/?CDC
Photo
Photo 1-1
 

2) The client should be aware that prior to 1976, factory-built homes in America were built only according to voluntary standards. Because this building was built prior to 1976, it may be significantly substandard in safety, efficiency, quality, durability, etc. Factory-built homes since 1976 have been required to comply with federal construction and safety standards (the HUD Code). This code is administered by the U.S. Department of Housing and Urban Development (HUD), and standardizes design, construction, energy efficiency, fire resistance, transportability, strength, and durability. It also mandates performance standards for the electrical, plumbing, air conditioning, thermal, and heating systems.

Grounds
Return to table of contents

Limitations: Unless specifically included in the inspection, the following items and any related equipment, controls, electric systems and/or plumbing systems are excluded from this inspection: detached buildings or structures; fences and gates; retaining walls; underground drainage systems, catch basins or concealed sump pumps; swimming pools and related safety equipment, spas, hot tubs or saunas; whether deck, balcony and/or stair membranes are watertight; trees, landscaping, properties of soil, soil stability, erosion and erosion control; ponds, water features, irrigation or yard sprinkler systems; sport courts, playground, recreation or leisure equipment; areas below the exterior structures with less than 3 feet of vertical clearance; invisible fencing; sea walls, docks and boathouses; retractable awnings. Any comments made regarding these items are as a courtesy only.
Site profile: Minor slope
Condition of driveway: Required repair, replacement and/or evaluation (see comments below)
Driveway material: Asphalt
Condition of sidewalks and/or patios: Appeared serviceable
Sidewalk material: Poured in place concrete
Condition of deck, patio and/or porch covers: Appeared serviceable
Deck, patio, porch cover material and type: Covered (Refer to Roof section)
Condition of decks, porches and/or balconies: Appeared serviceable
Deck, porch and/or balcony material: Wood, Concrete
Condition of stairs, handrails and guardrails: Appeared serviceable
Exterior stair material: Wood

3) Minor deterioration (e.g. cracks, holes, settlement, heaving) was found in the driveway, but no trip hazards were found. The client may wish to have repairs made for cosmetic reasons.
Photo
Photo 3-1
 

Exterior and Foundation
Return to table of contents

Limitations: The inspector performs a visual inspection of accessible components or systems at the exterior. Items excluded from this inspection include below-grade foundation walls and footings; foundations, exterior surfaces or components obscured by vegetation, stored items or debris; wall structures obscured by coverings such as siding or trim. Some items such as siding, trim, soffits, vents and windows are often high off the ground, and may be viewed using binoculars from the ground or from a ladder. This may limit a full evaluation. Regarding foundations, some amount of cracking is normal in concrete slabs and foundation walls due to shrinkage and drying. Note that the inspector does not determine the adequacy of seismic reinforcement.
Wall inspection method: Viewed from ground
Condition of wall exterior covering: Appeared serviceable
Apparent wall structure: Wood frame
Wall covering: Metal
Foundation/stem wall material: Not applicable, slab, manufactured or mobile home
Footing material (under foundation stem wall): Preserved wood

4) This structure was constructed with a "post and pier" foundation. No concrete block or poured-in-place concrete perimeter foundation was installed. Structures with post and pier foundations are typically prone to damage from earthquakes. Insurance companies or lenders may not insure or finance such structures. Consult with a qualified contractor or engineer to discuss options for installing a new foundation per standard building practices.
Photo
Photo 4-1
Photo
Photo 4-2
Photo
Photo 4-3
 

5) Trees were in contact with or were close to the building at one or more locations. Damage to the building can occur, especially during high winds, or may have already occurred (see other comments in this report). Recommend that a qualified tree service contractor or certified arborist remove trees as necessary to prevent damage to the building exterior.
Photo
Photo 5-1
Photo
Photo 5-2
Photo
Photo 5-3
 

6) The paint or stain finish in some areas was failing (e.g. peeling, faded, worn, thinning). Siding and trim with a failing finish can be damaged by moisture.Recommend that a qualified contractor prep (e.g. clean, scrape, sand, prime, caulk) and repaint or restain the building exterior where necessary and per standard building practices. Any repairs needed to the siding or trim should be made prior to this.
Photo
Photo 6-1
Photo
Photo 6-2

7) No poured-in-place concrete footings were visible below the piers supporting this manufactured home. Settlement can occur as a result. Consult with a qualified contractor to determine options for installing footings per standard building practices.

Roof
Return to table of contents

Limitations: The following items or areas are not included in this inspection: areas that could not be traversed or viewed clearly due to lack of access; solar roofing components. Any comments made regarding these items are made as a courtesy only. Note that the inspector does not provide an estimate of remaining life on the roof surface material, nor guarantee that leaks have not occurred in the roof surface, skylights or roof penetrations in the past. Regarding roof leaks, only active leaks, visible evidence of possible sources of leaks, and evidence of past leaks observed during the inspection are reported on as part of this inspection. The inspector does not guarantee or warrant that leaks will not occur in the future. Complete access to all roof and attic spaces during all seasons and during prolonged periods of all types of weather conditions (e.g. high wind and rain, melting snow) would be needed to do so. Regarding the roof drainage system, unless the inspection was conducted during and after prolonged periods of heavy rain, the inspector was unable to determine if gutters, downspouts and extensions performed adequately or were leak-free.
Roof inspection method: Traversed
Roof surface material: Corrugated plastic or fiberglass
Roof type: Flat or low slope
Condition of exposed flashings: Appeared serviceable
Condition of gutters, downspouts and extensions: Required repair, replacement and/or evaluation (see comments below)

8) One or more rubber or neoprene pipe flashings were loose or lifting. Leaks can result from windblown rain. This is a conducive condition for wood-destroying organisms. Recommend that a qualified person repair as necessary to prevent leaks. For example, by nailing flashings down and sealing as necessary.
Photo
Photo 8-1
Photo
Photo 8-2
Photo
Photo 8-3
 

9) Suggest extending gutters to get water away from house.

Electric
Return to table of contents

Limitations: The following items are not included in this inspection: generator systems, transfer switches, surge suppressors, inaccessible or concealed wiring; underground utilities and systems; low-voltage lighting or lighting on timers or sensors. Any comments made regarding these items are as a courtesy only. Note that the inspector does not determine the adequacy of grounding or bonding, if this system has an adequate capacity for the client's specific or anticipated needs, or if this system has any reserve capacity for additions or expansion. The inspector does not operate circuit breakers as part of the inspection, and does not install or change light bulbs. The inspector does not evaluate every wall switch or receptacle, but instead tests a representative number of them per various standards of practice. When furnishings, stored items or child-protective caps are present some receptacles are usually inaccessible and are not tested; these are excluded from this inspection. Receptacles that are not of standard 110 volt configuration, including 240-volt dryer receptacles, are not tested and are excluded. The functionality of, power source for and placement of smoke and carbon monoxide alarms is not determined as part of this inspection. Upon taking occupancy, proper operating and placement of smoke and carbon monoxide alarms should be verified and batteries should be changed. These devices have a limited lifespan and should be replaced every 10 years. The inspector attempts to locate and evaluate all main and sub-panels. However, panels are often concealed. If panels are found after the inspection, a qualified electrician should evaluate and repair if necessary. The inspector attempts to determine the overall electrical service size, but such estimates are not guaranteed because the overall capacity may be diminished by lesser-rated components in the system. Any repairs recommended should be made by a licensed electrician.
Electric service condition: Appeared serviceable
Primary service type: Underground
Service voltage (volts): 120-240
Estimated service amperage: 60
Primary service overload protection type: Circuit breakers
Service entrance conductor material: Not determined (components inaccessible or obscured)
System ground: Cold water supply pipes
Condition of main service panel: Appeared serviceable
Location of main service panel #A: Bedroom
Location of main disconnect: Breaker at top of main service panel
Condition of branch circuit wiring: Serviceable
Branch circuit wiring type: Non-metallic sheathed
Solid strand aluminum branch circuit wiring present: None visible
Ground fault circuit interrupter (GFCI) protection present: Yes
Arc fault circuit interrupter (AFCI) protection present: No
Smoke alarms installed: Yes, but not tested
Carbon monoxide alarms installed: Yes, but not tested

10) One or more electric receptacles (outlets) at the kitchen and/or bathroom(s) had no visible ground fault circuit interrupter (GFCI) protection, or the inspector was unable to determine if GFCI protection was present. If not GFCI-protected, receptacles in wet areas pose a shock hazard. Recommend that a qualified electrician evaluate and install GFCI protection if necessary and per standard building practices. General guidelines for GFCI-protected receptacles include the following locations:
  • Outdoors (since 1973)
  • Bathrooms (since 1975)
  • Garages (since 1978)
  • Kitchens (since 1987)
  • Crawl spaces and unfinished basements (since 1990)
  • Wet bar sinks (since 1993)
  • Laundry and utility sinks (since 2005)
For more information, visit:
http://www.reporthost.com/?GFCI
Photo
Photo 10-1
Photo
Photo 10-2

11) Branch circuit wiring installed in buildings built prior to the mid 1980s is typically rated for a maximum temperature of only 60 degrees Celsius. This includes non-metallic sheathed (Romex) wiring, and both BX and AC metal-clad flexible wiring. Knob and tube wiring, typically installed in homes built prior to 1950, may be rated for even lower maximum temperatures. Newer electric fixtures including lighting and fans typically require wiring rated for 90 degrees Celsius. Connecting newer fixtures to older, 60-degree-rated wiring is a potential fire hazard. Repairs for such conditions may involve replacing the last few feet of wiring to newer fixtures with new 90-degree-rated wire, and installing a junction box to join the old and new wiring.

It is beyond the scope of this inspection to determine if such incompatible components are installed, or to determine the extent to which they're installed. Based on the age of this building, the client should be aware of this safety hazard, both for existing fixtures and when planning to upgrade with newer fixtures. Consult with a qualified electrician for repairs as necessary.

Plumbing / Fuel Systems
Return to table of contents

Limitations: The following items are not included in this inspection: private/shared wells and related equipment; private sewage disposal systems; hot tubs or spas; main, side and lateral sewer lines; gray water systems; pressure boosting systems; trap primers; incinerating or composting toilets; fire suppression systems; water softeners, conditioners or filtering systems; plumbing components concealed within the foundation or building structure, or in inaccessible areas such as below tubs; underground utilities and systems; overflow drains for tubs and sinks; backflow prevention devices. Any comments made regarding these items are as a courtesy only. Note that the inspector does not operate water supply or shut-off valves due to the possibility of valves leaking or breaking when operated. The inspector does not test for lead in the water supply, the water pipes or solder, does not determine if plumbing and fuel lines are adequately sized, and does not determine the existence or condition of underground or above-ground fuel tanks.
Condition of service and main line: Appeared serviceable
Water service: Public
Location of main water shut-off: Building exterior, H2o shut off out back door to left
Condition of supply lines: Appeared serviceable
Supply pipe material: Not determined (inaccessible or obscured)
Condition of drain pipes: Appeared serviceable
Drain pipe material: Plastic
Condition of waste lines: Appeared serviceable
Waste pipe material: Plastic
Vent pipe condition: Appeared serviceable
Vent pipe material: Plastic
Sump pump installed: None visible
Sewage ejector pump installed: None visible
Type of irrigation system supply source: Public
Location of main fuel shut-off valve: At gas meter

12) One or more plumbing vent pipes terminated less than 6 inches above the roof surface below. Debris and/or snow can block vent pipe openings with such short pipes. Blocked vent pipes can cause sewer gases to enter living spaces. Recommend that a qualified person repair per standard building practices. For example, by extending pipe(s) to terminate at least 6 inches above the roof surface.
Photo
Photo 12-1
 

Water Heater
Return to table of contents

Limitations: Evaluation of and determining the adequacy or completeness of the following items are not included in this inspection: water recirculation pumps; solar water heating systems; Energy Smart or energy saver controls; catch pan drains. Any comments made regarding these items are as a courtesy only. Note that the inspector does not provide an estimate of remaining life on water heaters, does not determine if water heaters are appropriately sized, or perform any evaluations that require a pilot light to be lit or a shut-off valve to be operated.
Condition of water heater: Near, at or beyond service life
Type: Tank
Energy source: Natural gas
Estimated age: 9yrs
Capacity (in gallons): 30
Temperature-pressure relief valve installed: Yes
Location of water heater: Exterior closet
Hot water temperature tested: Yes, Hot
Water temperature (degrees Fahrenheit): ?
Condition of venting system: Appeared serviceable

13) The insulated jacket was damaged and should be replaced.
Photo
Photo 13-1
 

14) The estimated useful life for most water heaters is 8-12 years. This water heater appeared to be near this age and/or its useful lifespan and may need replacing at any time. Recommend budgeting for a replacement in the near future, or considering replacement now before any leaks occur. The client should be aware that significant flooding can occur if the water heater fails. If not replaced now, consider having a qualified person install a catch pan and drain or a water alarm to help prevent damage if water does leak.

Heating, Ventilation and Air Condition (HVAC)
Return to table of contents

Limitations: The following items are not included in this inspection: humidifiers, dehumidifiers, electronic air filters; solar, coal or wood-fired heat systems; thermostat or temperature control accuracy and timed functions; heating components concealed within the building structure or in inaccessible areas; underground utilities and systems; safety devices and controls (due to automatic operation). Any comments made regarding these items are as a courtesy only. Note that the inspector does not provide an estimate of remaining life on heating or cooling system components, does not determine if heating or cooling systems are appropriately sized, does not test coolant pressure, or perform any evaluations that require a pilot light to be lit, a shut-off valve to be operated, a circuit breaker to be turned "on" or a serviceman's or oil emergency switch to be operated. It is beyond the scope of this inspection to determine if furnace heat exchangers are intact and free of leaks. Condensation pans and drain lines may clog or leak at any time and should be monitored while in operation in the future. Where buildings contain furnishings or stored items, the inspector may not be able to verify that a heat source is present in all "liveable" rooms (e.g. bedrooms, kitchens and living/dining rooms).
General heating system type(s): Wood-burning fireplace or stove
General heating distribution type(s): None, individual heaters
Last service date of primary heat source: Undetermined
Source for last service date of primary heat source: None
Condition of furnace filters: N/A (none visible)
Condition of forced air ducts and registers: Appeared serviceable
Condition of venting system: Required repair, replacement and/or evaluation (see comments below)
Condition of cooling system and/or heat pump: None
Condition of controls: Appeared serviceable

15)   House has ventilation plumbed to all rooms, but central system was replaced with a gas wall unit.
Photo
Photo 15-1
 

Fireplaces, Stoves, Chimneys and Flues
Return to table of contents

Limitations: The following items are not included in this inspection: coal stoves, gas logs, chimney flues (except where visible). Any comments made regarding these items are as a courtesy only. Note that the inspector does not determine the adequacy of drafting or sizing in fireplace and stove flues, and also does not determine if prefabricated or zero-clearance fireplaces are installed in accordance with the manufacturer's specifications. The inspector does not perform any evaluations that require a pilot light to be lit, and does not light fires. The inspector provides a basic visual examination of a chimney and any associated wood burning device. The National Fire Protection Association has stated that an in-depth Level 2 chimney inspection should be part of every sale or transfer of property with a wood-burning device. Such an inspection may reveal defects that are not apparent to the home inspector who is a generalist.

16) Fireplace and flu had quite a bit of creosote build up should be cleaned could cause out of control fire in flu!
Photo
Photo 16-1
Photo
Photo 16-2
Photo
Photo 16-3
Photo
Photo 16-4

Kitchen
Return to table of contents

Limitations: The following items are not included in this inspection: household appliances such as stoves, ovens, cook tops, ranges, warming ovens, griddles, broilers, dishwashers, trash compactors, refrigerators, freezers, ice makers, hot water dispensers and water filters; appliance timers, clocks, cook functions, self and/or continuous cleaning operations, thermostat or temperature control accuracy, and lights. Any comments made regarding these items are as a courtesy only. Note that the inspector does not provide an estimate of the remaining life of appliances, and does not determine the adequacy of operation of appliances. The inspector does not note appliance manufacturers, models or serial numbers and does not determine if appliances are subject to recalls. Areas and components behind and obscured by appliances are inaccessible and excluded from this inspection.

Bathrooms, Laundry and Sinks
Return to table of contents

Limitations: The following items are not included in this inspection: overflow drains for tubs and sinks; heated towel racks, saunas, steam generators, clothes washers, clothes dryers. Any comments made regarding these items are as a courtesy only. Note that the inspector does not determine the adequacy of washing machine drain lines, washing machine catch pan drain lines, or clothes dryer exhaust ducts. The inspector does not operate water supply or shut-off valves for sinks, toilets, bidets, clothes washers, etc. due to the possibility of valves leaking or breaking when operated. The inspector does not determine if shower pans or tub and shower enclosures are water tight, or determine the completeness or operability of any gas piping to laundry appliances.
Location #A: Full bath, first floor
Location #B: 3/4 bath, Master bath
Condition of counters: Appeared serviceable
Condition of cabinets: Appeared serviceable
Condition of sinks and related plumbing: Appeared serviceable
Condition of toilets: Appeared serviceable
Condition of bathtubs and related plumbing: Appeared serviceable
Condition of shower(s) and related plumbing: Appeared serviceable
Condition of ventilation systems: Appeared serviceable
Bathroom and laundry ventilation type: Windows
Gas supply for laundry equipment present: Yes
240 volt receptacle for laundry equipment present: Yes

17) No accessible gas shut-off valve was visible within 6 feet of the gas-fired clothes dryer. This is a potential safety hazard when the appliance needs to be shut down quickly. Recommend that a qualified contractor install a shut-off valve per standard building practices.

18) Pictures of sinks and appliances
Photo
Photo 18-1
Photo
Photo 18-2
Photo
Photo 18-3
Photo
Photo 18-4
Photo
Photo 18-5
Photo
Photo 18-6
Photo
Photo 18-7
Photo
Photo 18-8
Photo
Photo 18-9
Photo
Photo 18-10

Interior, Doors and Windows
Return to table of contents

Limitations: The following items are not included in this inspection: security, intercom and sound systems; communications wiring; central vacuum systems; elevators and stair lifts; cosmetic deficiencies such as nail-pops, scuff marks, dents, dings, blemishes or issues due to normal wear and tear in wall, floor and ceiling surfaces and coverings, or in equipment; deficiencies relating to interior decorating; low voltage and gas lighting systems. Any comments made regarding these items are as a courtesy only. Note that the inspector does not evaluate any areas or items which require moving stored items, furnishings, debris, equipment, floor coverings, insulation or similar materials. The inspector does not test for asbestos, lead, radon, mold, hazardous waste, urea formaldehyde urethane, or any other toxic substance. Some items such as window, drawer, cabinet door or closet door operability are tested on a sampled basis. The client should be aware that paint may obscure wall and ceiling defects, floor coverings may obscure floor defects, and furnishings may obscure wall, floor and floor covering defects. If furnishings were present during the inspection, recommend a full evaluation of walls, floors and ceilings that were previously obscured when possible. Determining the cause and/or source of odors is not within the scope of this inspection.
Condition of exterior entry doors: Appeared serviceable
Exterior door material: Metal
Condition of interior doors: Appeared serviceable
Type(s) of windows: Vinyl, Metal, Multi-pane
Condition of walls and ceilings: Appeared serviceable
Wall type or covering: Drywall, Paneling
Ceiling type or covering: Tiles
Condition of flooring: Appeared serviceable
Flooring type or covering: Carpet, Vinyl, linoleum or marmoleum, Laminate

19) One or more window screens were damaged or deteriorated. These window(s) may not provide ventilation during months when insects are active. Recommend replacing window screens as necessary.
Photo
Photo 19-1
 


Photo
Photo X-1
Photo
Photo X-2
Photo
Photo X-3
Photo
Photo X-4
Photo
Photo X-5
Photo
Photo X-6
Photo
Photo X-7
Under deck structure
Photo
Photo X-8
Photo
Photo X-9
Photo
Photo X-10
Photo
Photo X-11
Unprotected gas line
Photo
Photo X-12
Photo
Photo X-13
Photo
Photo X-14
No cover on exterior plug
Photo
Photo X-15
Photo
Photo X-16
Photo
Photo X-17
Photo
Photo X-18
Should have GFCI plug at this location
Photo
Photo X-19
Photo
Photo X-20
Photo
Photo X-21
Photo
Photo X-22
Photo
Photo X-23
Build up of Creosote, definitely a fire hazard
Photo
Photo X-24
Roofing torn
Photo
Photo X-25
Tear in roofing
Photo
Photo X-26
Photo
Photo X-27
Photo
Photo X-28
Photo
Photo X-29
Rodent damage
Photo
Photo X-30
Rodent damage
Photo
Photo X-31
Photo
Photo X-32
Photo
Photo X-33
Photo
Photo X-34
Photo
Photo X-35
Photo
Photo X-36
Photo
Photo X-37
Photo
Photo X-38
Photo
Photo X-39
Photo
Photo X-40
Photo
Photo X-41
Photo
Photo X-42
Photo
Photo X-43
Photo
Photo X-44
Photo
Photo X-45
Photo
Photo X-46
Photo
Photo X-47
Photo
Photo X-48
Photo
Photo X-49
Photo
Photo X-50
Photo
Photo X-51
Photo
Photo X-52
Photo
Photo X-53
Photo
Photo X-54


The Parties Understood and Agreed as follows:

1. INSPECTOR GUARANTEES to perform a visual inspection of the home and to provide CLIENT with a written inspection report identifying the defects that INSPECTOR both observed and deemed material. INSPECTOR may offer comments as a courtesy, but these comments will not comprise the bargained-for report. The report is only supplementary to the sellers disclosure.

2. INSPECTOR agrees to perform the inspection in accordance to the current Standards of Practice of the National Association of Certified Home Inspectors posted at http://www.nachi.org/sop.htm.

3. CLIENT understands that the inspection will be performed in accordance to the aforementioned Standards, which contain certain limitations, exceptions, and exclusions.

4. The inspection and report are performed and prepared for the use of CLIENT, who gives INSPECTOR permission to discuss observations with real estate agents, owners, repair persons and other interested parties. INSPECTOR accepts no responsibility for use or misinterpretation by third parties.

5. INSPECTOR does not perform engineering, architectural, plumbing, or any other job function requiring an occupational license in the jurisdiction where the inspection is taking place, unless the inspector holds a valid occupational license, in which case he/she may inform the CLIENT that he/she is so licensed, and is therefore qualified to go beyond this basic home inspection, and for additional fee, perform additional inspections beyond those within the scope of the basic home inspection.

6. In the event of a claim against INSPECTOR, CLIENT agrees to supply INSPECTOR with the following: (1) Written notification of adverse conditions within 14 days of discovery, and (2) Access to the premises. Failure to comply with the above conditions will release INSPECTOR and its agents from any and all obligations.

7. HOLD HARMLESS AGREEMENT: CLIENT agrees to hold any and all real estate agents involved in the purchase of the property to be inspected harmless and keep them exonerated from all loss, damage, liability or expense occasioned or claimed by reasons of acts or neglects of the INSPECTOR or his employees or visitors or of independent contractors engaged or paid by INSPECTOR for the purpose of inspecting the subject home.

8. In the event that CLIENT fails to prove any adverse claims against INSPECTOR in a court of law, then the CLIENT will pay all legal costs, expenses and fees of INSPECTOR in defending said claims.


9. If any provision of this Agreement is declared invalid or unenforceable by any court, the remaining provisions will remain in effect. This agreement represents the entire agreement between the parties. No change or modification shall be enforceable against any party unless such change or modification is in writing and signed by the parties. This Agreement shall be binding upon and enforceable by the parties and their heirs, executors, administrators, successors and assigns. CLIENT shall have no cause of action against INSPECTOR after one year after from the date of the inspection.

10. Payment, by CLIENT or CLIENTs representative, is due in full at the inspection site, upon completion of the on-site inspection. The CLIENT will pay all legal and time expenses incurred in collecting due payments.




"A Home Inspection is a Non-Invasive Visual Examination of a Residential Dwelling. Components may include any combination of mechanical, structural, electrical, plumbing, or other essential systems or portions of the home, as identified and agreed to by the Client and Inspector, such as: Roof ~ Exterior ~ Basement / Foundation ~ Heating Cooling ~ Plumbing ~ Electrical ~ Fireplace ~ Attic & Insulation ~ Doors, Windows & Interior."
From NACHI Standards of Practice


"There are conditions that require the removal of some part of the building to observe, measure, or test otherwise concealed construction. Such intrusive inspections require some demolition and should be performed only with the permission of the owner and by experienced, qualified mechanics."
-From the U.S. Department of Housing and Urban Development's
Residential Rehabilitation Inspection Guide, 2000


- HOMES BEING INSPECTED DO NOT "PASS" OR "FAIL" -
A home inspector merely discloses his or her findings and reports those findings to the client. Everyone involved graduates to a state of higher learning, and the client can now make better informed decisions about the purchase of a home and its future needs of upkeep and repair.

Four key areas of most home/building inspections cover the exterior, the basement or crawlspace areas, the attic or crawlspace areas and the living areas. Inspectors typically will spend sufficient time in all of these areas to visually look for a host of red flags, tell-tale clues and signs or defects and deficiencies.

The inspected areas of a home/building will consist of all of the major visible and accessible electro-mechanical systems as well as the major visible and accessible structural systems and components of a building as they appeared and functioned at the time and date of the inspection.

Inspectors typically do not provide warranties or guaranties with their inspections and reports. Buyers should therefore not rely on the inspection as any form of insurance policy against any latent, hidden, concealed or future defects and deficiencies.

The following are also some key items that buyers should remember and consider when reviewing their inspection reports:
* Inspections are not code compliance evaluations.
* Inspection reports are not structural engineering reports.
* Systems and components that are off during the inspection are not tested or reactivated.
* Buyers should consult with and ask questions of owners and their representatives.
* Roof inspections and their components are typically done from eaves or street level with binoculars.
* Reports are confidential and are meant exclusively for buyers, and not brokers or owners.
* Inspectors typically will not find each and every defect in a building, hence buyers should anticipate future typical defects and deficiencies.
* Further evaluation by specialists is recommended for any areas showing defects/deficiencies.
* A final walk-through inspection should be carried out the day before closing by the new owners to double check the condition of the building.



Limitations:
I. An inspection is not technically exhaustive.
II. An inspection will not identify concealed or latent defects.
III. An inspection will not deal with aesthetic concerns or what could be deemed matters of taste, cosmetic, etc.
IV. An inspection will not determine the suitability of the property for any use.
V. An inspection does not determine the market value of the property or its marketability.
VI. An inspection does not determine the advisability or inadvisability of the purchase of the inspected property.
VII. An inspection does not determine the life expectancy of the property or any components or systems therein.
VIII. An inspection does not include items not permanently installed.
IX. These Standards of Practice apply only to homes with four or fewer dwelling units.

Exclusions:
I. The inspectors are not required to determine:
A. Property boundary lines or encroachments.
B. The condition of any component or system that is not readily accessible.
C. The service life expectancy of any component or system.
D. The size, capacity, BTU, performance, or efficiency of any component or system.
E. The cause or reason of any condition.
F. The cause for the need of repair or replacement of any system or component.
G. Future conditions.
H. The compliance with codes or regulations.
I. The presence of evidence of rodents, animals or insects.
J. The presence of mold, mildew or fungus.
K. The presence of air-borne hazards.
L. The presence of birds.
M. The presence of other flora or fauna.
N. The air quality.
O. The existence of asbestos.
P. The existence of environmental hazards.
Q. The existence of electro-magnetic fields.
R. The presence of hazardous materials including, but not limited to, the presence of lead in paint.
S. Any hazardous waste conditions.
T. Any manufacturer recalls or conformance with manufacturer installation or any information included in the consumer protection bulletin.
U. Operating costs of systems.
V. Replacement or repair cost estimates.
W. The acoustical properties of any systems.
X. Estimates of how much it will cost to run any given system.

II. The inspectors are not required to operate:
A. Any system that is shut down.
B. Any system that does not function properly.
C. Or evaluate low voltage electrical systems such as, but not limited to:
1. Phone lines.
2. Cable lines.
3. Antennae.
4. Lights.
5. Remote controls.
D. Any system that does not turn on with the use of normal operating controls.
E. Any shut off valve.
F. Any electrical disconnect or over current protection devices.
G. Any alarm systems.
H. Moisture meters, gas detectors or similar equipment.



III. The inspectors are not required to:

A. Move any personal items or other obstructions,
such as, but not limited to:

1. Throw rugs.
2. Furniture.
3. Floor or wall coverings.
4. Ceiling tiles
5. Window coverings.
6. Equipment.
7. Plants.
8. Ice.
9. Debris.
10. Snow.
11. Water.
12. Dirt.
13. Foliage.
14. Pets

B. Dismantle, open, or uncover any system or component.
C. Enter or access any area which may, in the opinion of the inspector, to be unsafe or risk personal safety.
D. Enter crawlspaces or other areas that are unsafe or not readily accessible.
E. Inspect underground items such as, but not limited to, underground storage tanks or other indications of their presence, whether abandoned or actively used.
F. Do anything which, in the inspector's opinion, is likely to be unsafe or dangerous to the inspector or others or damage property, such as, but not limited to, walking on roof surfaces, climbing ladders, entering attic spaces or negotiating with dogs.
G. Inspect decorative items.
H. Inspect common elements or areas in multi-unit housing.
I. Inspect intercoms, speaker systems, radio-controlled, security devices or lawn irrigation systems.
J. Offer guarantees or warranties.
K. Offer or perform any engineering services.
L. Offer or perform any trade or professional service other than home inspection.
M. Research the history of the property, report on its potential for alteration, modification, extendibility, or its suitability for a specific or proposed use for occupancy.
N. Determine the age of construction or installation of any system structure, or component of a building, or differentiate between original construction or subsequent additions, improvements, renovations or replacements thereto.
O. Determine the insurability of a property.
.